I am trying to see what the best approach is to retrigger the alarm horn after the operator has silenced it. As of now when an alarm comes in the operator hits the "up arrow" key, which we have a key macro to silence horn. Sometimes the alarm will go awhile before they even ack the alarm. So I was trying to figure out a way if they ignore this that after a period of time the horn will retrigger and go back off. I was looking at maybe a scheduler. I have tried it in a module just for that particular alarm by ack it through the code, and also disenabling it then reenalbing it but I am not sure that would be the correct way. I was looking for maybe a global way to do it. Anyone ever do anything like this?
Andre Dicaire
In reply to Andre Dicaire:
In reply to Bill Sayers:
In reply to Former Member:
In reply to Ben Bishop:
There is also an excellent primer on ISA 18.2, which you can find here: https://www.isa.org/store/alarm-management-a-comprehensive-guide-second-edition/116298. You may not have registered Colin's statement about being two years into an alarm rationalization process. This is not unusual and seems daunting, but the long term payoff is worth the effort. As Ben suggests, the "Top 10" lists from DeltaV Analyze will show the low-hanging fruit. In similar projects, I have managed to reduce the alarm rate about 80% by addressing the top 10 most frequent alarms, all of which turned out to be nuisance alarms.
In reply to Bill Thackston: