Consider the following scenario with a PID block:• SP=0; PV=0; OUT=0; BAL_TIME=0; OUT_LO_LIM=0; OUT_HI_LIM=100; STRUCTURE=PI action on error, D action on PV; MODE=ROUT; GAIN=2• The PV and the BKCAL are forced to 0, GoodCascade• In one scan, switch the PID to RCAS and give it a setpoint of 10• What I expected to happen in the first scan is that PID/OUT jumps instantly to GAIN*ERROR=20 (and then starts ramping upwards because of the I action)• What happens instead is that a much smaller “kick” is given, around 8. Do you know why?Do you know which parameters to look at, what might be limiting the initial kick?
I also tried first putting it in RCAS and only a couple of seconds later giving it the new setpoint, but the initial OUT is still smaller than I expected.