Mechanical items, such as shut down valves, isolation valves, control valves, actuators and other pneumatic accessories, if selected and sized properly during the design stage to meet process parameters/conditions, fluid comparability, environmental conditions, etc., will typically follow a bathtub curve aging lifecycle.
The bathtub curve consists of three periods: an infant mortality period with a decreasing failure rate followed by a normal life period (also known as “useful life”) with a low, relatively constant failure rate and concluding with a wear-out period that exhibits an increasing failure rate.
Failures during infant mortality are highly undesirable and are always caused by issues such as material defects, design blunders, errors in assembly, etc. Normal life failures are normally considered to be random cases of “stress exceeding strength.” However, many failures often considered normal life failures are infant mortality failures. Wear out is caused by fatigue or depletion of materials, such as lubrication depletion in bearings. A product’s useful life is limited by its shortest-lived component.
Emerson’s Fisher valve and actuation technology products have been in the field for many decades. Design improvements made over time as products mature, increase ruggedness and reliability to provide extended life in the field. In fact, I just got a request from customer for a spare part (linkage between positioner and actuator) for a Fisher control valve supplied in 1974. This customer still insists that this valve is working fine but that the external linkages need replacement due to corrosion. You can imagine the reliability of these mechanical items.
Manufacturers and producers are typically focused on reliability centered maintenance (RCM) to increase performance in plant availability. Reliability engineering concepts has been in these industries for a long time. However, reliability has become more prominent in the past two decades due to the use of electrical/electronic/programmable logic devices. These are used for field assets and control system, which have been migrating towards smart microprocessor-based technology for better accuracy, more precise control, easier operation and maintenance, diagnostics, and more.
Unlike mechanical failures, electrical, electronic or microprocessor-based failures are categorized to ensure failure data can be organized in a consistent way.
ISA Technical report ISA-TR84.00.02-2002 –Part 1 talks about two failure modes:
For these failure modes:
Mechanical components’ life is a function of applications, process fluid, fluid physical properties, operational history, maintenance records, environmental conditions, test philosophy, etc. However, preventive maintenance practices play an important role in extending the life of mechanical items. Especially if they are re-built correctly each time during a shutdown/outage/turnaround back to original manufactures specifications.
The same is applicable for electrical, electronic or microprocessor-based field devices, where preventive maintenance, specifically of software parts, should be done at each interval recommend by the manufacturer, to extend their useful lives.
During failure modes, effects, and diagnostic analysis (FMEDA) for EUC (Equipment under control), the failure rates are calculated and rough benchmarks can be established for the life expectancy as per below formula.
Mean time to failure (MTTF) = Integration of Reliability function with respect to time from 0 to infinity limit = ∫ R(t) dt
or simply
1/(sum of all the part failure rates) = 1 /λ {Assumption: Single or series of components with constant failure rates}
To summarize, mechanical equipment such as shutdown valves, control valves, actuators, and accessories such as positioners are designed keeping in mind a plant’s life of around 25 years. Though you may not find any written or stated document from any supplier or manufacturers since mechanical deterioration depends on many parameters like internal process-related conditions or external environmental conditions, operating media (air, hydraulic fluid, etc.), proper care exercised during application selection & sizing, and more.
Visit the Valves, Actuators & Regulators section on Emerson.com for more on these technologies and their designs for long life. You can also connect with other final element experts in the Valves, Actuators & Regulators group in the Emerson Exchange 365 community.