• Not Answered

DeltaV insight license

Hi

I have two questions about deltav insight:

1- what is different between deltv insight basic and deltav insight DST base?

2-number of DST is base on PID loops or System DST (for Digital signals (DI, DO) also we need order it)? 

Thanks

3 Replies

  • The answers to these questions are best received from your representative. He should know and is payed for!
  • These questions are answered in the DeltaV Insight Product Datasheet available on the Emerson Process website.
    www2.emersonprocess.com/.../DV_PDS_Insight.pdf

    To answer you question, Insight Basic is a single user license assigned to a specific Workstation.
    - Provides base functionality available in DeltaV Tune and Inspect (pre v9.3).
    - Does not include Performance Reports, Tuning Recommendations,
    - Adaptive Tuning or other capabilities enabled by embedded process learning. It provides loop tuning and basic Inspect functionality.

    The system wide DeltaV Insight is licensed based on the number of Analog OUT DST's, which represents a system's control loops. You purchase a base license to cover your system AO size, and can increase this with Scaleup licenses as needed. With DeltaV Insight, you can access the application from any DeltaV station.

    Prior to v12, Insight was licensed by general size, as shown in the data sheet.

    Andre Dicaire