Removing access to a main display but keeping the diagram

Hi,

I need to remove access, for the operators, to one of our main display screens, at the moment it is available from the 'Display Directory' and 'Open Main Display' folder both on the toolbar.

I don't want to lose any of the items in the display, should we decide to re-use the display.

any help is greatly appreciated

  • In reply to Lee W.:

    Lee,

    I remember the chuckle I received when asking "how do you delete a graphic in DeltaV" to one of our Emerson Local Business Partner reps after we received our first DeltaV system years ago.

    It would be nice if Emerson made it easier, but you need to delete the graphic from at least 3 or 4 directories. And you would want to do this on each operator station as well. Where I previously worked, we used a command script on the proplus that would allow the user to input the graphicname to be deleted and delete from al required directories on all servers and workstations.

    ...DeltaV\DVData\Graphics-iFix\Pic\graphicname.grf
    ...DeltaV\DVData\Graphics-iFix\Pic\Backup\graphicname.grf

    ...DeltaV\DVData\YellowPages\Graphics-iFIX\Pic\graphicname.grf.Z
    ...DeltaV\DVData\YellowPages\Graphics-iFIX\Pic\Backup\graphicname.grf.Z