Hello All,
We are looking at communicating with a CompactLogix PLC through an Allen-Bradley 1769-SDN Scanner Module. We have been able to establish the communication with the PLC and are able to pass along data both ways, but are now having some communication issues with some devices on the DeviceNet network. We have had a few devices (Powerflex drive and some E3 overloads) give a fault status due to a communication problem. The Powerflex Drive is giving a Port 5 Fault and the E3 Overloads are giving that the communication status is bad. It requires us to cycle power on the buckets (and disconnect the DeviceNet cable to cycle power to the E3’s), and then we are able to restart the motors. This problem initially started when we first connected the PLC and it went away when we disconnected the PLC, which leads me to believe that our problem stems from the addition of the PLC on the Network.
I am just beginning to troubleshoot fully, as we did not have the communication established until last week. Any help, or other suggestions, would be greatly appreciated.