Hello;
WE are using DeltaV 11.3. We are facing problem with Trends. Before telling you the current problem I would like to brief about the problems wefaced & resolved.
In our Module class, in history collection tags has been assigned as Modulename(e.g. LIC101/PV.CV or TI101/Pv.cv) Due to which we were not getting trends on Chart builder. Then we changed this as Module name/Module type/Pv.cv (e.g LIC101/PID1/pv.cv , TI101/AI1/PV/CV) With this modification we found the Individual Trends that open from Faceplate are not appearing. Then we open D:/DeltaV/DVData/Chart/Lib Location where all the standard windows for the chart are stored. we find the Standard Window used for our Project & Made changes there also for Open Loop(Previous(MOD/PV.CV & NOw( MOD/AI1/PV.CV) & Closed loops(Previous Mod/PV.CV & Now MOD/PID1/PV.CV Same is applicable for SP.CV & Out.cv). Now Individual trend were appearing correct.
Now In group Trends (In chart Builder ) Open Loop (e.g TI101) Trend is appearing & giving Historical trend as it is(TI101/AI1/PV.CV) But Closed Loop Trends are still taking path as LIC101/PV.CV) Instead of Taking path as (LIC101/PID1/PV.CV). I am unable to find where shall i make this change so that Close loop trend will also appear on Chart Builder. Pl. help..