screens problems.

I have version 11.3.1 delta V, I have a problem, screens are not updated in the workstations, the  YPMaster in the workstations  is not pro plus.Control stations YPmaster appears as one of the same workstation, thanks for your help

2 Replies

  • Open yellowpagesdiag.exe on the workstation. In the Auto-Update diagnostics client observe the Master Server field and messages after performing a download to the workstation.
    If you can't discern anything meaningful from this diagnostic client, performing workstation configuration on the workstations should reset the master server assignment. Make sure you know the DeltaVAdmin password before starting workstation configuration.
  • Before running workstation config. you could check auto-update service (DeltaV->Engineering->Auto-Update Service) and make sure all the checkboxes are checked for this station. (Click 'set' to confirm.)
    Also check if the primary and secondary networkcables are connected correctly. YP uses the secondary network only for copying displays and setup data, afaik.