Proplus Power Failure

My Deltav 12.3.1 Proplus got down because of Power failure. Now I am not able to open DV explorer. It gives RPC error. Documents say database is corrupted and nothing can be done. Can anyone suggest way to recover the database in this situation.

Regards,

Rajat

11 Replies

  • And your last fhx or DB backup was when?
     
    Click to show quoted text
    From: rajatkumarsingh [mailto:bounce-rajatkumarsingh@community.emerson.com]
    Sent: Friday, August 29, 2014 10:45 AM
    To: DeltaV@community.emerson.com
    Subject: [EE365 DeltaV Track] Proplus Power Failure
     

    My Deltav 12.3.1 Proplus got down because of Power failure. Now I am not able to open DV explorer. It gives RPC error. Documents say database is corrupted and nothing can be done. Can anyone suggest way to recover the database in this situation.

    Regards,

    Rajat

  • Hi,

    You could try to do a rerun workstation configuration....?

    read : technet.microsoft.com/.../2007.07.howitworks.aspx

    You could also try to do a repair of the databse with database administration..

    Do you see any strange fault messages in the Logs?

    Are all of the services and processes runninng?

    have you restared the computer after the crash?

    Niklas Flykt 

    Klinkmann Oy

    Key Account Manager safety products

    nikfly@gmail.com

  • In reply to AdrianOffield:

    No backup since last 3 weeks.

  • In reply to Niklas Flykt:

    Thanks Niklas.

    Yeah restarted the server. All services running. No strange logs as well.

    I will go through the RPC error resolution - link shared.

    Appreciate your help.

  • In reply to AdrianOffield:

    3 weeks old. Lot of work done after that.

  • In reply to rajatkumarsingh:

    here something from this site:

    community.emerson.com/.../3952.aspx

    www.linkedin.com/.../RPC-server-unavailable-when-opening-1270757.S.91830308

    Niklas Flykt 

    Klinkmann Oy

    Key Account Manager safety products

    nikfly@gmail.com

  • In reply to Niklas Flykt:

    Niklas , going through as suggested.

    Will update once done.

  • In reply to rajatkumarsingh:

    HI,

    you should really, really invest in UPS:ses.

    You never know what willl happen if you cut the supply in the right moment, it may never start again.. or you have to reinstall everything :p

    Niklas Flykt 

    Klinkmann Oy

    Key Account Manager safety products

    nikfly@gmail.com

  • In reply to Niklas Flykt:

    I agree with the UPS.  I have a dedicated UPS for the ProPlus and I have the system and database back up daily at 7 am.

  • In reply to mikesteiger:

    I would suggest purchasing on a UPS that has monitoring capability and communication capability to send an alert.  This will help prevent this from happening.  

    If you have acronis, you can also do an image of your DeltaV Pro+.  This will really speed up your recovery.

    Keep us updated on this situation.  

  • Is auto export enabled? Are there any FHX's in the import-export folder?

    Sent from my iPod

    On 29 Aug 2014, at 17:41, "rajatkumarsingh" <bounce-rajatkumarsingh@community.emerson.com> wrote:

    No backup since last 3 weeks.