Hi
I thought it was a simple task to show on a picture the text of module alarm, but I found no way, all day long.i.e. : In MY_MODule, I have configured an alarm using "Change_of_state" type (COS), and I have choosen the text "STOP_PUMP" as alarm text.
In my picture, if I use "DVSYS.MY_MOD/STOP_PUMP.A_CV", the text returned is "COS" = The alarm type, but not the alarm text.I'm looking to put a DataLink on my picture that shows "STOP_PUMP" and not "COS"
I have tried many and many other syntaxes with no success.
I had a look to the alarm banner, but all is refering to THISUSER datas, that have other kind of attributes.
Regards. Jack
In reply to Jack_France:
Jack
You can use the DeltaV alarm summary object on a graphic or faceplate. When you drop this object onto the graphic you can select which module or modules are shown in it and also which columns are to be displayed.
The options are Description, Alarm, Message etc.
Not sure which version of DeltaV you are using but this object is available in 11.3.
Steve Linehan