Phase Logic Module with permissive?

Is it possible to develop phase logic module containing permissive condition as that of equipment module?

If so kindly brief me on the set of changes which is required to be made.

  • Phase logic modules include a FAIL_MONITOR.  You can configure any nature of continuous logic in the FAIL_MONITOR to either send the PLM to hold (traditionally) or keep the PLM RUN_LOGIC from starting by setting the AUTO_ADVANCE or PHASE_ENABLE parameters dynamically.