Has anyone ever made or does Emerson have a EDS file for this module?
Hi Tim,
Not sure what you're asking. The module is a standard I/O module for DeltaV and as such doesn't need an EDS. The DeviceNet devices you connect to the module will require their own EDSs but the module is just another I/O card as far ad DeltaV is concerned.
Bruce Brandt
In reply to Bruce Brandt:
Tim,
In addition to Bruce's information, the DeltaV card can ONLY act as a DeviceNet "Master"/Scanner. That's the reason there is no eds file as it can't be used as a "slave" device.
Is there something we can help you with regarding the use of the DeviceNet card?
In reply to Tyler Anderson:
Thanks for replying. Hey Bruce hope you are doing well!
Many of the Rockwell products have EDS's for their scanners. I was just wondering if there was one for DeltaV since I am configuring the network using RSnetwork for devicenet. Does the card only provide Polling as an option? Can it do strobe, cyclic or COS?
In reply to Timothy Sells:
From what I see in books on line it only does polling.