I have Asco Solenoid valve that requires 78 mA to open. Can the IS DO charm open this valve. I've been getting mixed information from other sources.
Looking at the product data sheet, it says the IS DO charm can drive a maximum of 45mA at 11 VDC. Looks like this solenoid may require other protection means (P&F isolators are available that will drive up to 100 mA at 11VDC) if you want to keep that circuit intrinsically safe.