Delta V live Display Sets - change Font Titles

Hi do you know how can I change the size of the titles in the display sets?

2 Replies

  • Hi Jose,

    1. Go to the Layouts section in Graphics Studio and open the layout you are using.
    2. In the Styling section of the layout, scroll down to the Toolbars section.
    3. If you are using a layout generated by Graphics Studio, the Font property will be linked to a standard.
      1. Open the standard by CTRL+Click on the standard
      2. Change the font to your desired values
      3. Save and publish
      4. Refresh DeltaV Live to see those changes reflected.
    4. If you are using custom Layouts, follow the same directions from above, but the Font property may or may not be linked to a standard.
      1. If it is not linked to a standard, you can change it directly on the property field. Then save the layout and publish it
      2. If it is linked to a standard, follow the procedure in step 3.

    Best regards,

    Camilo Fadul

    Camilo Fadul | DeltaV Solution Marketing Director

    https://www.linkedin.com/in/cfadul

  • In reply to Camilo Fadul:

    Thanks it works