I assigned new SD alarm for a PI and when testing the DO in the logic, everything works as it should. When checking voltage with output is false I still have 120VAC.
Andre Dicaire
In reply to Andre Dicaire:
In reply to gbilly :
In reply to Matt Stoner:
At this state I still have voltage present, physically at the charm 120 VAC.
Most Digital Outputs, CHARMS included, will have some leakage current detected with no load attached. If you are reading the CHARM with no field wires or load attached, it would not surprise me that you might read voltage with a DVM (Digital Volt Meter). This leakage current is so small that it does not produce the output to turn on.