On a simple PID control module where a pressure transmitter is controlling a valve output for pressure control we had an odd experience. Historically the AI OUT_SCALE and XD_SCALE did not match the actual pressure transmitter scale. The module was updated to have the correct OUT_SCALE and XD_SCALE in the AI block and then set the PID PV_SCALE to match. We made the change to all of these parameters to from 0-100, to 0-4000. Upon changing these parameters the rate at which the PID out changed to control the valve became significantly slower. The tuning parameters were not modified and the production use was not changed.
Does the PV_SCALE get used in the calculations for the PID output ? Or what would cause the sudden change in the execution of the block ? Also, this is all with Fieldbus devices.
In reply to Junggyu Yu:
In reply to MPHymel: