WRONG TERMINATION OF CONTROL TO PUMPS

Hello and warm greetings to distinguished members of this forum.

This is the issue am currently addressing. We have two GLYCOL INJECTION PUMPs(A & B), which are displayed on the DCS faceplate, so when a start command is initiated on PUMP B,PUMP A will be running in the field, When viewed from AMS, I discovered the PUMPS are attached to profieldbus DP series 2 card from which it is routed to the MCC unit motor control center. so what can i do to correct this control wrong termination?

1 Reply

  • Hi
    we have two glycol injection Pumps : (A AND B)

    TAGS ARE SUPPOSE PUMP A
    PUMP B
    START COMMAND INITIATED ON PUMP B ,
    PUMP A WILL BE RUNNING IN THE FIELD
    YOU CAN TRY THIS ONE : YOU CAN CHANGE THE START COMMAND PARAMETER
    FOR PUMP B TO A BY USING THIS METHOD AS :

    IN Deltav explorer select the module for Pump B AND
    IN THAT CHANGE THE START COMMAND PARAMETER FROM PUMP B TO PUMP A AND THEN
    DOWNLOAD THAT PARTICULAR MODULE.
    Hope this will be use full

    Regards

    Prashant