Frequent locking of DeltaV Explorer,any solution?
Services Forum
Blogs
Library/Resources
Members
Tags
More
Cancel
Create New Post
Comment or Question? Become a member of this Emerson Exchange 365 group. Click here to join.
Recent Services Discussions
Milton Pollard
2 Jul 2019 3:30 PM
DeltaV Live Conversion Service Now Available
0 Replies
CuriousDuncan
9 Mar 2019 8:07 PM
FIRST OUT LOGIC IN INTERLOCK
2 Replies
Tiffany Tang
5 Feb 2019 10:43 PM
VIDEO: Eliminate Limit Cycles & Loop Interactions in your Plant
0 Replies
Zachary Sample
21 Jan 2019 11:27 PM
How One Common Mistake is Ruining Simulator Maintainability
0 Replies
Shirley Marquardt-Tynan
11 Dec 2018 8:01 PM
Steam System Coordination for Optimized Returns
0 Replies
<
>
Similar Posts
DeltaV Operator Station Lock Ups
DeltaV Explorer
DELTAV EXPLORER
DELTAV EXPLORER
UNABLE TO OPEN DeltaV EXPLORER
Share
Not Answered
Frequent locking of DeltaV Explorer,any solution?
4 Replies
Matt Stoner
29 Feb 2024 2:21 PM
This is most likely a scheduled cleaning of the database where no connections are allowed and you have to wait until this completes. Rebooting the Proplus may solve this but you should log a call with Global Service Center (GSC) if the reboot doesn't solve your issue and you are not trying to connect during the time the cleaning is scheduled to run or someone is manually starting it.
Nadhiya
29 Feb 2024 2:29 PM
In reply to
Matt Stoner
:
Rebooting the proplus allows us to make changes at the moment, but we are facing a recurring locking issue every two weeks, want to know which task is holding that lock.
Matt Forbis
29 Feb 2024 3:04 PM
In reply to
Nadhiya
:
As Matt indicates, this is most likely a scheduled clean of the database. This would show up in the windows task scheduler on the Pro+. Generally database cleans need to be performed periodically, though it can be scheduled at a time when no one is typically on the system.
Nadhiya
29 Feb 2024 3:26 PM
In reply to
Matt Forbis
:
thanks for the reply, Instead of daily cleaning at midnight, we will change that to weekly schedule & monitor the system.