Emerson Exchange 365
Sign-In / Register
Site
Sign-In/Register
Community Hubs
DeltaV Community Connect
Ovation Users Group
Asset Management
Measurement Instrumentation
Valves, Actuators & Regulators
Fluid Control & Pneumatics
Electrical Components & Lighting
Welding, Assembly & Cleaning
Perspectives
Emerson Automation Experts
Conferences
San Antonio 2025
Düsseldorf 2024
Immerse - Anaheim 2023
Grapevine 2022
Services
Services Forum
Frequent locking of DeltaV Explorer,any solution?
Services Forum
Blogs
Library/Resources
Members
Tags
More
Cancel
Create New Post
Comment or Question? Become a member of this Emerson Exchange 365 group. Click here to join.
Recent Services Discussions
Todd Brase
13 Dec 2019 8:17 PM
VIDEO: Improving Control Room Operations with Emerson’s iOps Workspace Solution
0 Replies
David Lee
18 Nov 2019 8:35 PM
VIDEO: Ensuring Operator Effectiveness with Conscientious Control Room Design
0 Replies
Emerson Exchange News
27 Sep 2019 12:23 AM
DeltaV success on a shoe-string budget
0 Replies
Emerson Exchange News
26 Sep 2019 9:20 PM
Up-front attention eases integration tasks for Shell
0 Replies
Darwin Logerot
24 Sep 2019 1:59 PM
VIDEO: The Five Keyword Approach to Help Avoid Alarm Flooding
0 Replies
<
>
Similar Posts
DeltaV Operator Station Lock Ups
DeltaV Explorer
DELTAV EXPLORER
DELTAV EXPLORER
UNABLE TO OPEN DeltaV EXPLORER
Share
Not Answered
Frequent locking of DeltaV Explorer,any solution?
4 Replies
Matt Stoner
29 Feb 2024 2:21 PM
This is most likely a scheduled cleaning of the database where no connections are allowed and you have to wait until this completes. Rebooting the Proplus may solve this but you should log a call with Global Service Center (GSC) if the reboot doesn't solve your issue and you are not trying to connect during the time the cleaning is scheduled to run or someone is manually starting it.
Nadhiya
29 Feb 2024 2:29 PM
In reply to
Matt Stoner
:
Rebooting the proplus allows us to make changes at the moment, but we are facing a recurring locking issue every two weeks, want to know which task is holding that lock.
Matt Forbis
29 Feb 2024 3:04 PM
In reply to
Nadhiya
:
As Matt indicates, this is most likely a scheduled clean of the database. This would show up in the windows task scheduler on the Pro+. Generally database cleans need to be performed periodically, though it can be scheduled at a time when no one is typically on the system.
Nadhiya
29 Feb 2024 3:26 PM
In reply to
Matt Forbis
:
thanks for the reply, Instead of daily cleaning at midnight, we will change that to weekly schedule & monitor the system.