3051S transmitter operating temperature

Hi,

The 3051S manual has the following temperature limits

Ambient -40 to 185 °F (-40 to 85 °C)

With LCD display(9): -40 to 175 °F (-40 to 80 °C)

I'd like to know if the failure rates in the FMEDA report remain the same if the transmitter is operated continuously at the higher end of these limits? If my transmitter is operated at a constant 70 Deg C would the failure rates be the same as a transmitter operated at 20 Deg C and are there any other considerations for operating transmitters at elevated temperatures in safety applications such as useful life?

regards

Paul

  • Paul,
    Sorry for the delayed reply.
    Can you send me an e-mail at brad.burton@emerson.com?
    I'd like to get into some detail on this so we can best answer your question.
    Brad
  • Hi Paul,

    For the short answer: it is expected that the failure rates for a transmitter operating at a consistently higher ambient temperature would be different than a transmitter operating at consistently average or lower ambient temperatures.

    For some additional explanation, the FMEDA report has a few statements in relation to your question:

    “Some industrial plant sites have high levels of stress. Under those conditions the failure rate data is adjusted to a higher value to account for the specific conditions of the plant… If a user has data collected from a good proof test reporting system such as exida SILStatTM that indicates higher failure rates, the higher numbers shall be used” (Section 4.2)… “The stress levels [used to derive FMEDA failure rates] are average for an industrial environment and can be compared to the exida Profile 2 with temperature limits within the manufacturer’s rating. Other environmental characteristics are assumed to be within manufacturer’s rating” (Section 4.3).

    Note that Profile 2, in Appendix C, shows that this report assumes an average ambient temperature of 25 deg C. Since it is impossible to take into account all of the varying operating conditions these devices may operate in, the FMEDA report published by exida is based on average conditions and the assumption that the devices are always operated within their specified limits. The failure rates published in the FMEDA report are only valid for the Useful Life of the product, so Useful Life is certainly an appropriate consideration to take into account for any transmitter in a safety application; the Useful Life assumes that the device is maintained (and replaced when appropriate) according to IEC 61508/61511 - this includes operating within the manufacturer ratings, as you noted above.

    I hope this is helpful - please feel free to reach out here with additional questions, or to me (megan.wiens@emerson.com) or Brad (see previous reply) via email.

  • In reply to Megan Wiens:

    Good Day, I'm wondering we have a Delta V cabinet and the temperature is 50.7 Deg C. I'm hopeful to figure out how to attach a thermal scan of the unit to see if this is within operating parameters or if I have a problem. We found this was higher during this quarterly Thermal Scan