3144P Temprature transmitter model code query

Hi there,

I have a 3144P transmitter with model number  3144PD2F1NAA01M5WR3C4Q4GMXS

Can anyone tell me what the C4Q4GMXS is as I can not see where to get it.

Thanking the community in advance

Gerard

  • Hello Gerard

    Below is a breakdown of these option codes:

    • C4: 5-Point calibration
    • Q4: Calibratoin Certificate
    • GM: A size mini, 4-pin male (minifast) Conduit Connection

    We do not have an "XS" option on the 3144P.  Perhaps this is option "XA", which means that the transmitter was assembled to a sensor at the original time of order and build at an Emerson factory.  

    Below is a link to a the full product datasheet for the Rosemount 3144P Temperature Transmitter, which can help you understand what each option code means.  

    https://www.emerson.com/documents/automation/product-data-sheet-rosemount-3144p-temperature-transmitter-en-73128.pdf

    Thank you,

    Michael Olivier, VP Temperature and Corrosion products

  • In reply to Michael Olivier:

    Hi Michael,
    Thanks for the reply and the clarification of the model number.
    I just assumed that the naming convention would continue on, not jump back for extra options.
    Many thanks
    Gerard