I'm trying to configure an SNMP link to monitor an older Liebert UPS with no success.
I've had no issue establishing links to CISCO Switches to monitor port status as it would appear that Ovation DS 3.5.0 came pre-loaded with MIBs to accommodate.
Below is a snippet of the "snmp_config" file that I loaded using Ovation Developer Studio.
All of the configured points are showing bad quality. What am I missing?
I was able to connect via snmp to the UPS using a standard MIB browser application on the same host workstation.
Adding to Tim's feedback, I'll also mention that Ovation owners/users have access to detailed networking whitepapers on the Ovation Users' Group website. The list of whitepapers includes one on SNMP.
In reply to Greg Schirm:
Thanks Tim!
Now, do I need to modify the "mib.txt" file located here: C:/ovation/snmp/mibs/mib.txt in order to reference my newly added mib for the UPS?
In reply to tim fu:
In reply to James Hall: