hi to all
we are using ovation 3.3.1 in our plant as control system
we have an analog input signal from controller 16 on common database server and we want to transfer this signal to other controller on unit #1 database server.
how this can be done?
I don't know the answer to your question, but I have forwarded it to some of our engineers. If you would like to share more information, I could try to have an Ovation engineer contact you directly.
Hi Majed,
I'm service engineer at EPM Dubai office.
Pelase send me your phone numer so I'll call you and help you over the phone.
'It is not much compcated process but several steps are required: you need to delete point at the existing location then create the same point at new location.
Clear and load affeted controllers are required, also database server has to be cleared and loaded in order to update online distributed database.
In reply to mziarko:
HI mziarko
This is my phone number 00966504449621
In reply to Majed Alhussain:
If you can give me a reference it will be very helpful.
this my e-mail: msulaiman2@swcc.gov.sa