I have a PID controller feeding a Splitter FB with two FFAO. The Splitter FB setup is default 0,50,50,100 to 0,100,0,100 with OUT_1 holds. Recently with the PID in Manual Mode and 0% output, the valve #1 output changed to 100% open. Based on Event file, there were number of FF I/O failures typically lasting less than one second (PID Execution is at 1 second) with no impact, but once FF I/O failure exceed 1 second then, the Splitter ignored the PID output command and proceed to Y12!
Has anyone seen this issue? Any solution?
Regards;
Hassan
Andre Dicaire
In reply to Andre Dicaire:
Andre;
Thank you for your detailed response.