Background: I have a SX controller residing in a controller cabinet which is always powered. The controller is connected to 2 sets of CIOCs which are residing in individual Skid cabinets (eg: A_CIOC in skid A cabinet , B_CIOC in skid B cabinet). At any one time only 1 of the skid is required to run hence to save on electricity we turn off the power to the other skid. We always get a standing alarm for SX controller saying the Skid CIOC is not communicating for the powered down skid. Is there anyway we can use any conditional alarming to remove this standing alarm?
In reply to Steve Linehan:
In the Exploring DeltV on the containers look for the "I / O Network" then look for the CIOC that you want to disable the alarm then select it and in the right side of the Exploring DeltaV your gona see "CHARMS" and "Hardware Alarms" make a double click on "Hardware Alarms" then you will see 4 typs of alarms, in your case make other 2 click´s on FAILED_ALM and uncheck the Enable box and make a download of the CIOC