Increasing a Dataset array size

I have a running system that uses a serial card to read and write data between DeltaV and ControlLogix.  Initial configuration was set up on the Logix side to pass an array of 64 Integers and a Dataset of only 32 on the DeltaV side. My question is this if I increase the Dataset Properties / PLC / Number of Values from 32 to 64 and download the controller, will it disrupt the communications between the two systems?

Thank you,

2 Replies

  • Are you using Block Write or Individual writes in the dataset? Are you able to create a test Dataset with a test module and try this out so you can confirm your Module Logic doesn't result in a reset of values due to a momentary BAD status on the data set.

    Hopefully someone on the forum has more experience with the Serial Card.

    Andre Dicaire

  • In reply to Andre Dicaire:

    Hi Andre,

    Thanks for the reply. I will dig deeper into your question about the dataset. I was confident there wouldn't be an issue but errored on the side of caution and had them shut down the area of the plant before I performed the download. Everything went smoothly, and it was over in seconds, and the data appeared to ride through the download. I will have to do some testing in the future to verify unless someone else has move experience and can comment. I believe it is good practice to wait for a shutdown for this type of scenario.

    Thanks again