Parallel Prompts

Hello Everybody,

I am looking to understand if any of you had done parallel prompts (Prompt 1 and Prompt 2) configuration or potential possible ways to do in a DeltaV phase class. We have a requirement where we need to display two prompts at the same time during the process. Acknowledging Prompt 1 would repeat a loop of the phase and acknowledging the prompt 2 will end the phase.

Best Regards,

Arun

1 Reply

  • A single phase can only have one prompt active in the Batch Executive at a time, You will need to develop another method or use a single prompt (i.e. Yes to Repeat or No to End Phase)