I have the Analog tracking block (AT) connected to PID track input. PID track is enabled. I have a tracking condition that puts the controller in manual.
Books Online States:
When any tracking condition's T_L_OUT_Dnand T_HOLD_MANn parameters are True, the mode of the target analog block wired to OUT_D is set to Manual.
But when I check the Hold in Manual Block. Upon activation of tracking condition, The PID Mode goes from Auto/Auto to Auto/Local Override instead of Manual.
In control options, Tracking is enabled and Track in Manual is disabled. Even if I enable both the issue remains.
Any Suggestions?
Thanks
In reply to Trista VanDerVeeken:
The first out trapping as well as the driving of the mode to manual when enabled will only be done if the output has changed.
Make sure your PID output is outside of this range before triggering the condition in your testing.