Hello DeltaV community,
I need some help please. I am having some issues setting up a Modbus tcp interface to a prosoft on an controllogix rack, using a vim2 card on an Sx Controller. I am able to see that the VIM is communicating successfully with the prosoft (VIMnet configuration is correct and device is showing to be connected & online). But the data I am reading into my registers is gibberish. Not sure if it is a setting on the virtual serial card or a register is off, etc.
Following is configuration on the prosoft end for the analog read and the analog write data points-
1. Registers on Prosoft for 'read' datapoint- x000 & 0001; Data Type- Real; Modbus Function- FC 3 (read holding registers); 2 16-bit registers
Note- this is a parameter that DeltaV is reading over Modbus and it is 32-bit floating point
2. Register on Prosoft for 'write' datapont- x2000 & x2001; Data Type- Real; Modbus Function- FC 16 (write multiple holding registers); 2 16-bit registers
Note- This is a setpoint that DeltaV is sending over Modbus and it is a 32-bit floating ponit
Following is configuration I used for my datasets on the deltav device on serial card -
1. dataset 1- Input Data; DeltaV Data Type- Floating point with Status; Device Data Type- 3; Data Start Address - 0; Number of values- 1
2. dataset 2- Output Data; DeltaV Data Type- Floating point with Status; Device Data Type- 3; Data Start Address - 2000; Number of values- 1
I am reading data, but it doesn't match the values on the other end. Not sure if my registers are offset or if my datatype is wrong or what??
Thanks in advance!