I am referencing an OUT1 (CALC output) parameter in "CTRL2" in the RELAY-MODULE from the control module DUT_TEST1 which is located in another controller "CTRL1" (but same Area).
When referencing another parameter from the CTRL1 (i.e. CTRL1/I01/C07/OINTEG) no issues are present and the status is delivered to the control module assigned to CTRL2. In the same control module I reference the CALC block without success.
Has anybody else experienced the same behavior?
Thanks for your help.
Here the referenced parameters in RELAY-MODULE:
In reply to Matt Forbis:
Hi Matt,
I have tried that already. Both Controllers have their setup data loaded and I am also able to read the parameter successfully with watchit.
What bothers me the most is that this used to work without any issue.
In reply to Matt Stoner:
In reply to GregorP:
Andre Dicaire
In reply to Andre Dicaire:
Hi Andre,
We are talking about an external ref:
I tried the 'RELAY-MODULE/DEV_INT.#REF' which gave me the following result:
And 'RELAY-MODULE/DEV_INT.CST' returns:
According to books-online this means that the "module is not configured". Which seems odd since I have downloaded the setup data on both controllers.
I did manage to create a module with an external reference to the same path which was assigned to the Pro plus :
I however need the parameter in the sequence function chart module that is assigned to the Controller 2.
The last test I did was to add an external reference in the CTRL2 module pointing to an AI block on CTRL1 which also did not work:
So it seems that the only control module having trouble to communicate with other control modules is the one assigned to the controller 2.