Hi all, so I read in several of documents that stated "communication between the I/O cards and the control module shall be via well-secured communication link with high capacity of data transfer and speed not less than 2 Mbps"
kindly please advice, is it that statement can comply with DV, please info exactly the speed of DV's communication.
thanks and best regards
Al Amin
Al Amin, please refer to Page 2 of this Product Data Sheet (PDS) which states network speed for DeltaV Area Control Network (ACN).
Quoting from the PDS:
"The DeltaV ACN supports the use of auto-negotiated 10-half, 100-half, 10 full, and 100-full duplex communications where the industry standard auto-negotiation process determines the highest speed at which two devices will communicate with each other.."
Hope this helps.
In reply to MC_Chow:
In reply to al amin:
Andre Dicaire