hi,
I am able to communicate with Mycom CPM 153 PA and able to read all inputs from transmitter but when i am trying to write from Control module not able ?
Please help.
Andre Dicaire
In reply to chip.burge:
In reply to Andre Dicaire:
In reply to Hemant ikhar:
CPC 30 profibus manual.pdf
Status is also good,
In attached manual Pg no 15. Control CPC (SP_D),
We are able to write 0000 0001 in Control CPC (SP_D), and it gets reflected in deltav Diagnostics that value of signal is decimal 1.
We are able to write 0000 0010 in Control CPC (SP_D), and it gets reflected in deltav Diagnostics that value of signal is decimal 2 .
But the PH assembly does not move to Measure Position & Service position.
Do I need to send some more values to CPM 153 through Control CPC (SP_D) or do i have to enable some other bits so that PH assembly will start moving?