DeltaV 11.3 configuration for Siemens DP/PA link (153-2) and coupler (157)

Hi

I am trying to connect DeltaV to two pH analysers(Mettler Toledo PA400) through DP/PA link (153-2) and coupler 157.

I created gsd file (for the sip58052 using the PA40's GSD ) from gsd tool .After downloading the card, the BF1 LED on153-2 is ON and BF LED on 157 is ON. All other LEDs are fine.  Diagnostics on DeltaV are GOOD and recognises the 153-2 as master. But still cannot read the analyser values in DeltaV

Are there any empty slots that we need to configure in DeltaV? Which slot will be for my pH analyser? (PA address is 23,24 ) 

Please guide.

Thanks in advance

Amit

1 Reply

  • Hi Amit,
    as a first step have a look to this thread about gsd file creation: http://community.emerson.com/process/emerson-exchange/operateandmanage/deltav/f/50/t/564
    Maybe the GSD file creation was not correct?
    I think you should create all the slots defined within the GSD file and the device should be connected when you dowload in order to start the communication...
    I will face a similar task in the near future so I will track your thread...