I have five terminal servers installed in a customer site. Each server is configured identically. On TSERV2 - 4 the batch executive status shows normal. On all the sessions on TSERV1 the batch executive status shows STOPPED. This status will not change if the Exec is started or stopped. All TSERV sessions look at the same simplex exec. Other DeltaV services work normally such as Workspace, DeltaV Explorer, Control Studio and Batch Historian. All services are started the same on all 5 machines. Has anybody seen this type of behavior before?
In reply to Ray Emerson:
In reply to Steve Linehan:
In reply to chessley:
Ran the ServPwd and reset to standard. No joy with this solving issue. I then tried regall /register and this set the password again at the end of regitering services. Hey presto problem solved. Thanks everyone for your help and suggestions.