Hello Everyone
I have the project used the VIM2 to communication with Rocwell PLC (Controllogix , Compactllogix) and any Device via EtherNet IP ( Gas detector and etc)
Details for DeltaV (DeltaV12.3 Version , DeltaV M-Series Hardware, Redundant VIM2 and IOD-4112 Rockwell PLC EtherNet/IP Driver for DeltaV VIM2.)
I already read manual from Mynah for configuration Class3 UCMM (Encapsulated DF1) connection and Class1 (ENBT) connection.
(Ethernet/IP Master Driver for DeltaV Virtual I/O Module for both Simplex and Redundant Ethernet/IP Version 3.3.3x and 3.3.5x, Apirl 2007)
I plan to choose the Class3 UCMM to communication with Rockwell PLC.
My question as details below,
1.For the Rockwell PLC, If we do configuration in DeltaV for mapping data to communication via EtherNet IP, PLC should be configuration for mapping data refering data from DeltaV ? ( Refer Mynah Manual)
2.For the Rockwell PLC, If they configuration Class3 UCMM (Encapsulated DF1, Use Map PLC/SLC message) connection and datatype is DINT or DINT[#] (DINT array) this datatype can communication with VIM?
3.For any Device Gas detector, They used Ethernet /IP driver and hardware form Field Server, How to configuration to communication with this Device and This device need any license from Mynah?
Could everyone to share your idea and your advice to me.
Thank you & Best regards
Suttiporn.
In reply to lazy_engineer:
In reply to Suttiporn:
How many files we can Map PLC/SLC messages in RSLogix 5000 Software ?
EX Refer PLC/SLC Mapping popup
File Number Name
1 INT[20] Data 1
2 INT[5] Data 2
3 INT[5] Data 3
4 INT[100] Data 4
5 INT[100] Data 5
These are above data in PLC/SLC Mapping Table popup seperate for Discrete Input , Discrete Output , Analog Input and Analog Output.
The limitation of data for Mapping PLC / SLC depend on VIM data specification, Am I right for this information ?
Best regards
Suttiporn
Hello lazy_engineer
For my understand, If I have data map like table below.
We will count the data map to 5 data ( 5 data = 5 dataset in DeltaV), Am I correct ?
We have 8 - 9 packages link to this VIM.(The packages used minimum 5 data map per each package).
If we have 9 packages minimum data map = 9 * 5 = 45 data map or 45 Dataset in DeltaV, These data packages are possible link to one VIM (Maximum = 128 Data or 128 Dataset in DeltaV), My understand is correct or not ?.
If do you have any advice please let us know.
Thank you
Thank you for all of your answer, These are good information for developing the our project.