Parse, OK and Cancel buttons getting invisible

Parse, OK and Cancel buttons gets invisible whenever I click on any of the buttons. I have formatted my system and reinstalled the Deltav, then too problem is there.
  • Can you be more specific?  Which application within DeltaV are you inquiring about?

     

    Did you mean Pause (not Parse), Ok, and Cancel? 

     

    Youssef El-Bahtimy | Systems Integration Technologist
    PROCONEX | 103 Enterprise Drive | Royersford, PA 19468 USA
    Proconex Office: 610 495 2970 | Cell: 267 275 7513
  • have you installed your DeltaV on Laptop or Virtual Machine?

    specially, in DeltaV Rev11 i had this problem and all Parse, Ok and cancel get invisible whenever i clicked on any buttons. i suggest to install the DeltaV in a PC.

    as i checked, it happens whenever the screen resolution is changed, specially in Laptop or a virtual machine.

  • Pouya, u r correct DeltaV is installed in a Laptop.
    But it's working in my other Laptop, this issue is coming in this one Laptop only.
  • In reply to Mayank Bhatewara:

    Right click on a empty area in the desktop and then click on "Screen Resolution"

    2.  Click on the "Make text and other items larger or smaller" link

    3.  Select the display resolution

       -Smaller  = 96 dpi (100%)

    4.  Log off and then re-logon or restart the computer to apply the changes.

    Hope that helps

  • In reply to ekilkenny:

    very good, the problem is solved with this solution. Thank you ekilkenny