I'm going to install some controllers and I/O's and I need to make a calculation for the size of the Bulk Power supply. Someone has like a table specifying the consumption of each card, or an instalation guide for these purpose??
Thanks for the help!!!
ypiedra
Recommended reading:
DeltaV™ S-series and CHARMs Hardware Reference (D800040X012)
page 148 - Sizing the System Power Supply (24 VDC)
page 148 Sizing the AC to 24 VDC Bulk Power Supply
page 149 -DC current requirements for S-series I/O
There's a table in Books On Line as well