I've created a custom alarm list which shows all standing alarms within the last 12 hours. Does anyone know of a script to automatically print out the custom alarm list on DeltaV 11.3.1?
You can do this with a schedule inside a picture that is always open (p.e. The toolbar) This schedule you can Set the trigger to 12 hours. What you Must know is that you write the schedule in the usersettings of the Desired machine. ( a Exempel is in the usersettings marked with REM)
In reply to scdrummer:
reviewed the usersettings vb code and unable to find the example code. please could you paste the code?
In reply to Stuart Jolley:
The Sample Code isn't in the usersettings, only a section that Persenning a line with a *.evs command to activate your schedule. The schedule you must design in the DeltaV operate (schedule section at the bottom of the tree leftside the picture) for Exempels go to the Books online