Charms not displaying anymore

I was trying to figure out why one of the transmitters was only reading 3.5V. Thought I set all appropriate properties on the charm and I hit Rebuild Hierarchy. Now I can't find any of the Charms that it previously show. How can I get this back?

Before I could see all of them on AMS Device Manager (Device Connection View). I would then double click DeltaV Network 1 and I would be able to see all my devices connected but now I can't. Is there a way to get back to this?

4 Replies

  • Without knowing what version of AMS, it's going to be hard to give more than a general troubleshooting step. However, if nothing has changed with regards to the setup, doing a Terminate Services and restart the AMS Servers on the machine with the DeltaV interface is always a good first step. If that simple step doesn't resolve it, I would always suggest opening a call with the GSC, however if I knew what version of AMS you are running, I can give you a few more things to check.
  • In reply to Matt Forbis:

    Honestly, I don't even know how to find this information out for further help. There was one guy working on this and he's no longer here to help out so I tried to fix the first problem and came across another. So, if you can also provide with help on figuring out the version, I can send that information as soon as I get it.
  • In reply to Valentin Revuelta :

    In AMS Device Manager, go to Help > About AMS Device Manager. At the very top will be a version, such as 14.5 FP1 Build 035, for example. Also in there would be the System ID in the box at the bottom in the form of 0000-0000-0000. Both of these pieces of information would also be required for the GSC to guide you through the troubleshooting process.
  • In reply to Matt Forbis:

    The version we have here is the 14.5 FP2 Build 038