Hello
Recently we have been having ACN COMM events filling up the process history. The events recorded indicated that its been switching back to primary and secondary. Is there anyway to narrow it down to see if its the Primary or the secondary network connection that has the problem?
Thanks
Shri
Andre Dicaire
In reply to Andre Dicaire:
We constantly have ACN switchovers. We have a large facility and the response from Emerson has been that "some" ACN switchovers are expected. When I feel like they are getting excessive then I have found that exporting the event log, sorting on the ACN_COMM parameter, and then I use a pivot table in excel to help me figure out which device is having the most issues.