Hello All,
I am an engineering coop helping out with installation of a Delta V system. Ive come here to se if I could get a little information from the pros. I am designing a small WIOC installation and have a question about the redundant field link antennas. The question has to do with both placement of the antennas and if both antennas are working with the network at the same time. I will be placing the antennas at the top of a boiler building and was wondering if I could place the antenna on opposite ends of the roof to expand the network. I wasnt sure if the redundant WIOC and antenna were "on call" or an active part of the network at all times. I appreciate any help that I can get.
Thank You
Ryan Betts
Welcome to the community, Ryan. I am going to share your post in the DeltaV group as well. Cheers!
Best Regards,
Rachelle McWright: Business Development Manager, Dynamic Simulation: U.S. Gulf Coast
In reply to Ben Bishop:
I agree with Ben. Like the 1420 gateway, they should be mounted at the same height and be spaced between 1m to 3m horizontally. This is to ensure that they provide identical coverage for the wireless field network and to help eliminate coverage gap in the event of a switch over. Only one of them is actively transmitting at any one time, while the other is passive.
Thanks for your expertise, Ben & Jonas.
Hello All, I am an engineering coop helping out with installation of a Delta V system. Ive come here to se if I could get a little information from the pros. I am designing a small WIOC installation and have a question about the redundant field link antennas. The question has to do with both placement of the antennas and if both antennas are working with the network at the same time. I will be placing the antennas at the top of a boiler building and was wondering if I could place the antenna on opposite ends of the roof to expand the network. I wasnt sure if the redundant WIOC and antenna were "on call" or an active part of the network at all times. I appreciate any help that I can get. Thank You Ryan Betts
Craig Abbott - Wireless Specialist (South Eastern Australia)
In reply to Scott Pries:
Super problem-solving & collaboration going on in Wireless this week! Thanks for adding to the discussion, Craig and Scott. :)