As technologies advance through the adoption phases and into mainstream use, a common set of questions usually emerges. For example, as the IEC 62591 WirelessHART communications standard has moved from its introduction to the market in 2007 to present day, its use has increased widely across industries, geographies and applications. We’ve chronicled many of these stories in the wireless category of this blog.
Dale Perry Wireless Services Manager
…self-organising protocol utilising a time-synchronised, self-organising, and self-healing mesh architecture.
From the article, I’ll highlight a few of the most common questions I see in my travels through the social networks, and leave the rest for you to read if you’re interested.
How far the wireless communications can travel is a common question. Dale responds:
The transmission distance between two wireless devices is a function of the antenna type and the distance the antenna is above the ground or the structure of the installation. The specified distance is 225 m for a standard antenna mounted 1,8 m above the ground/structure. Optional high gain antennas with transmission distances up to 1 km are available and should be mounted a minimum of 3,4 m above the ground/structure. Since WirelessHART is a self-organising mesh technology with each radio able to communicate with all other radios, networks can cover much longer distances through “hopping” whereby transmitters closer to the gateway relay data for those further away.
Battery life for wireless instrumentation is another common question. He explains:
Contrary to most articles that seem to highlight only update rates affecting battery life, the radio actually consumes little power. Most of the power consumption in a device takes place when making the measurement. The more complicated the measurement or the algorithm to calculate the measurement, the more power is consumed. For example, a vibration measurement might require up to 60 000 samples per seconds for many seconds which takes a lot of power and will result in a shorter battery life. Conversely, a measurement to sample a voltage in a sensor will take very little power which equates to a longer battery life. Manufacturers have an online battery life estimator so users can approximate power draws and corresponding battery life for various measurement applications.
About the need for any special maintenance, Dale answers:
Wireless devices have the same maintenance and calibration requirements as wired devices because they use the same sensor technology as their wired equivalents. The only added maintenance is battery replacement, but this is more than offset by the elimination of wire and cable maintenance in most applications.
Read the article to find answers to other common questions including:
You can also connect and interact with other wireless experts in the Wireless group of the Emerson Exchange 365 community.
The post Answering Common Questions about Wireless Instrumentation appeared first on the Emerson Process Experts blog.