Similar Posts
Output POPup Window Problem in PID faceplate
Faceplate template update problem on DeltaV 8.4
Faceplates
Faceplate
faceplate help
Share
Faceplate Problem.
Hello...
I have a faceplate pushpin related some problems.
On the site faceplate pushpin are properly showings on ews and 1 operator system in run and edit mode.
But two No's operator stations faceplate pushpin are showing in runmode only.
3 Replies
PRASHANT-MUTTEPAWAR
20 Nov 2018 9:11 AM
Faceplate pushpin for all the stations should show always on run mode only.
girishbm1
20 Nov 2018 3:26 PM
Hi,
Try following:
1) Make sure that you have same faceplates on all workstations. Try coping the known good/working faceplate on the workstation where you have problem and see if it works.
2) Check if the visibility of pushpin group is set to "TRUE" in edit mode. It may be invisible in edit mode if the group visibility is set to "FALSE"; you need to scan the objects via system tree in DeltaV operate to find the pushpin group in that case. The pushpin functionality will not work in edit mode but you should be able to see the pushpin group/symbols in edit mode.
Regards,
Girish
Matt Forbis
24 Nov 2018 6:31 PM
In reply to
girishbm1
:
In addition, if it's not working on a few machines, but is on others, you might need to update the temp copies of the displays that allow the push pins to work. To do this, in DeltaV Operate, the DeltaV Utilities toolbar has a button called "Updated Popup Pictures" (second from the right I believe) that will update all the temp copies on that machine. For the pushpins to work, there has to be a temp copy for each one to pin. The default behavior is 3 temp copies, allowing you to have 4 modules using the same faceplate open at once.
Thanks,
Matt