Emerson Exchange 365
Search
User
Site
Search
User
State
Not Answered
Replies
1 reply
Subscribers
5483 subscribers
Views
8132 views
Users
0 members are here
Recent DeltaV Community Connect Discussions
Invalid String
1 Sep 2023 8:40 AM
DeltaV Simulate V15 Virtual Machine Help
3 Replies
Y H
28 Aug 2023 6:41 PM
DeltaV comms to Wonderware Historian
1 Reply
Invalid String
26 Aug 2023 8:21 PM
M Series Serial Card - Series 2 | Bad status | Reads work and writes don't?
2 Replies
Yogeshwar Patil
21 Aug 2023 1:18 PM
Facing Issue with Hotfix installation DeltaV_1431_WS_28_CSS
2 Replies
Jenny La Bounty
15 Aug 2023 5:40 PM
Bult Export Interlock Cause & Effect
2 Replies
<
>
Similar Posts
DCS FacePlate Setpoint increment by tenths
Dynapar Incremental Encoder Integration Into DeltaV
Automatically Increment Batch ID When New Batch is Created
Pulse Counter
Loss in weight counter
Share
Not Answered
increment/decrement counter
dear all,
how can i create a increment/decrement counter in SIS?
1 Reply
Neil Castro
13 Dec 2017 12:57 AM
I have created a simple increment/decrement counter SIS module.
Following are the parameters.
#Inputs
INC = When this parameter transitions from false to true the COUNT parameter increments by 1.
DEC = When this parameter transitions from false to true the COUNT parameter decrements by 1.
#Output
COUNT = is the total count.
Note: The COUNT parameter does not become negative.
Following is a link to an FHX file that contains the module (SIS_CNT).
drive.google.com/open
Hope this helps.