Emerson Exchange 365
Search
User
Site
Search
User
State
Not Answered
Replies
1 reply
Subscribers
5483 subscribers
Views
8118 views
Users
0 members are here
Recent DeltaV Community Connect Discussions
Adam Villhauer
30 Nov 2023 4:29 PM
Recommendations for EIOC Network Switches.
2 Replies
M_ASIM_B
21 Nov 2023 8:03 PM
Cannot Connect to The DeltaV Database Server
8 Replies
Luis G. Rodriguez
20 Nov 2023 7:56 PM
DeltaV IDDC
3 Replies
chrisslattery
14 Nov 2023 4:48 AM
Version control error when trying to commission wireless gateway
2 Replies
TreyB
13 Nov 2023 10:15 PM
Live Control Tag/Module
11 Replies
<
>
Similar Posts
DCS FacePlate Setpoint increment by tenths
Dynapar Incremental Encoder Integration Into DeltaV
Automatically Increment Batch ID When New Batch is Created
Pulse Counter
Loss in weight counter
Share
Not Answered
increment/decrement counter
dear all,
how can i create a increment/decrement counter in SIS?
1 Reply
Neil Castro
13 Dec 2017 12:57 AM
I have created a simple increment/decrement counter SIS module.
Following are the parameters.
#Inputs
INC = When this parameter transitions from false to true the COUNT parameter increments by 1.
DEC = When this parameter transitions from false to true the COUNT parameter decrements by 1.
#Output
COUNT = is the total count.
Note: The COUNT parameter does not become negative.
Following is a link to an FHX file that contains the module (SIS_CNT).
drive.google.com/open
Hope this helps.