Emerson Exchange 365
Search
User
Site
Search
User
State
Not Answered
Replies
1 reply
Subscribers
5482 subscribers
Views
8052 views
Users
0 members are here
Recent DeltaV Community Connect Discussions
s_brwn
10 Jun 2025 4:09 PM
Charms Diag Health Status
1 Reply
Prasanth Gopalakrishnan Nair
10 Jun 2025 11:44 AM
A_PV Changed without A_COMMAND
0 Replies
Horst
6 Jun 2025 4:58 AM
Restore parameter values after de(re)comissioning of controller
2 Replies
Abhi
5 Jun 2025 5:20 PM
Connecting Power Flex 755 Drive with DeltaV PK Controller via 20-750-ENETR Module
3 Replies
rhamlin
3 Jun 2025 7:11 PM
PHV embedded chart in DV Live
6 Replies
<
>
Similar Posts
DCS FacePlate Setpoint increment by tenths
Dynapar Incremental Encoder Integration Into DeltaV
Automatically Increment Batch ID When New Batch is Created
Pulse Counter
Loss in weight counter
Share
Not Answered
increment/decrement counter
dear all,
how can i create a increment/decrement counter in SIS?
1 Reply
Neil Castro
13 Dec 2017 12:57 AM
I have created a simple increment/decrement counter SIS module.
Following are the parameters.
#Inputs
INC = When this parameter transitions from false to true the COUNT parameter increments by 1.
DEC = When this parameter transitions from false to true the COUNT parameter decrements by 1.
#Output
COUNT = is the total count.
Note: The COUNT parameter does not become negative.
Following is a link to an FHX file that contains the module (SIS_CNT).
drive.google.com/open
Hope this helps.