I am having troubles running Delta V reporter. I can search for the tags on the ap station but when i go to run the reporter or "Try It" it says a problem occurred( pictured below).
I am logged onto admin on both. could use some suggestions. Thanks
check from here:
socialkb.suite-sol.com/.../STANDALONE_hist_coll.ditamap
Niklas Flykt
Klinkmann Oy
Key Account Manager safety products
[email protected]
In reply to Niklas Flykt:
no luck
In reply to jaym_DA:
Do you have a workstation or domain enviroment?
Check that the folder that you are going to read have sharing rights.
This is a workstation enviroment and the deltaVHistory folders where my data sets are all shared.
Check that you have all the users in the appstation as you do in the Prostation.
Try to download the workstation.
Might be that you are missing some user/rights that you would need to connect to the database?
I checked and all the users on the proplus station are on the Apstation. I then put DeltaV Reporter on the APStation and tried it from there. And i basically got the same message.
I downloaded to the ap station and setup data to the pro plus.
Try if you can acess the folderin the target machine from Proplus
The DeltaV Reporter user scheduling reports must have access to the Scheduled Tasks folder (C:\Windows\Tasks, by default).
C:\Windows\Tasks
To use DeltaV Reporter from a non-DeltaV workstation in a domain, a two-way trust relationship must be configured between the DeltaV domain and the domain of the non-DeltaV workstation using remote access.
By default, Excel as a COM object can only be activated by the Administrator, System, or Interactive accounts. Therefore, it is possible that a scheduled report will fail to run correctly under the following conditions:
To prevent this possibility, complete the following steps to edit the DCOM configuration settings for the Microsoft Excel Application object: 0 comments
Component Services/Computers/My Computer/DCOM Config
For a scheduled report to run successfully on a DeltaV or non-DeltaV workstation, the user specified in the Run as field of the Scheduled Report Properties dialog of DeltaV Reporter must be logged on, either locally or remotely through a connected or disconnected session, at the time the Task Scheduler attempts to execute the scheduled report task.
The DeltaV Reporter user scheduling reports must be included in the User Rights Assignment list of users with the Log on as a batch job policy. To check this setting, use Control Panel to open the Local Security Policy settings window, and then select Local Policies/User Rights Assignment in the console tree.
Local Policies/User Rights Assignment