Hi Forum
I struggle a bit around the DCC Permissive configuration together with an EDC.
Assume the motor has Left/Right mode and Star/Delta on a simple control module without EQM or Unit-Phase.
Operator shall be able to start a motor from Off to Left or Right in Star only. After 5 seconds in confirmed Star, the State for the same direction should be permitted to set to Delta or Off. Once in confirmed Deltav the only permissive for the motor shall be Off and not Star.
Once the motor run in any direction, It must be confirmed Off first for 10 seconds before the direction can change in Star first and then to Delta.
The EDC can handle all this nice states, better than with a huge logic and the old DC. How to configure now the DCC Permissive for the above conditions? Provox Guys remeber a little bit the DCD Point with this EDC :)
If any of the Permissive condition is false then the DCC/P_OUT_D is false. This is normal because only one of the permissive conditions will be true. Solong as EDC/PERMISSIVE_D is 1 then I still can change to any other state, with the EDC/DEVICE_OPT:Permissive to any state.
So, How does the EDC know which DCC Permissive or State is valid?
Actual I have following configured in the Permissive conditions of the DCC:
CND1 : Off State : '^/EDC1/PV_D.CV' > 0
CND2 : Left Star : '^/EDC1/PV_STATE.CV' = '$edc_pv_states_MLR:Confirmed OFF' with Delay on = 10
CND3 : Left Delta : '^/EDC1/PV_STATE.CV' = '$edc_pv_states_MLR:Confirmed LEFT STAR' with Delay On 5
CND4 : Right Star : '^/EDC1/PV_STATE.CV' = '$edc_pv_states_MLR:Confirmed OFF' with Delay on = 10
CND5 : Right Delta : '^/EDC1/PV_STATE.CV' = '$edc_pv_states_MLR:Confirmed RIGHT STAR'
Sure can I do now create a bunch of Logic round but Why it don't work with the DCC/EDC combination?
Thank You for Help and Best Regards, Michael