Emerson Exchange 365
Search
User
Site
Search
User
State
Not Answered
Replies
1 reply
Subscribers
5479 subscribers
Views
8052 views
Users
0 members are here
Recent DeltaV Community Connect Discussions
Rishi
1 Apr 2025 8:04 AM
Best Practices for Thin Client Time Synchronization – Seeking Experiences
0 Replies
GaryL
30 Mar 2025 5:39 PM
VIM 2 and Modbus TCP/IP S-Series Controller
8 Replies
LostEngineer0
7 Mar 2025 4:39 PM
Left mouse click problem
2 Replies
dikshitsh
6 Mar 2025 4:50 PM
Unable to restore Pro plus database from Restore option available in DV database Administration
4 Replies
Kent
5 Mar 2025 1:57 PM
Version 15 FP2 and Rockwell
4 Replies
<
>
Similar Posts
DeltaV Live - Restore Database Error Message
BulkEdit error message: WARNING: Required data does not exist on line 2 - module_name
Assistance Request for DeltaV Error Messages (See screenshots)
Eleborate the SK_CANTINSTALLHOOK error message
Verbose error messages in VBA
Share
Not Answered
DeltaV Live error message-does anyone have any idea about the error message?
1 Reply
Joshua Granger
10 Mar 2023 5:25 PM
Any given user can only have one instance of DeltaV Live running at a time. If you are able, log in as an engineering account (i.e. dvmanager) and go to the Windows Desktop. From there, open Task Manager, go to details, and close all open instances of the DeltaV Live process (I don't recall the executable name). Then, log back into the account you are trying to use and try opening DeltaV Live again.