Emerson Exchange 365
Search
User
Site
Search
User
State
Not Answered
Replies
1 reply
Subscribers
5484 subscribers
Views
8408 views
Users
0 members are here
Related Posts
DeltaV Live - Restore Database Error Message
BulkEdit error message: WARNING: Required data does not exist on line 2 - module_name
Assistance Request for DeltaV Error Messages (See screenshots)
Eleborate the SK_CANTINSTALLHOOK error message
Verbose error messages in VBA
Share
Not Answered
DeltaV Live error message-does anyone have any idea about the error message?
1 Reply
Joshua Granger
10 Mar 2023 5:25 PM
Any given user can only have one instance of DeltaV Live running at a time. If you are able, log in as an engineering account (i.e. dvmanager) and go to the Windows Desktop. From there, open Task Manager, go to details, and close all open instances of the DeltaV Live process (I don't recall the executable name). Then, log back into the account you are trying to use and try opening DeltaV Live again.